Postby Wayne on Thu Jul 01, 2010 11:45 pm

jjthefridge wrote:Hi,

just after plug sealed water proof, seems really good

j.j.


Oh I know the one, its really watertight (inline on the cable).




Nope, never took it out of the box. But, the salesperson said this tent was super easy to set up; even in windy conditions...
User avatar
Wayne
Site Admin
Site Admin
 
Posts: 4890
Images: 484
Joined: Thu May 28, 2009 11:31 pm
Location: Derbyshire
Shelter: One of each

Advertisement

Re: Electrics and tents

Postby valleydaddy on Thu Jul 08, 2010 4:30 pm

just got the last one out of B&Q in Cardiff

look a good bit of kit, will definately be of use and easy to roll up and store etc

thanks for the heads up on this topic folks ;)
One day the wife will understand the need to go mountainbiking at least twice a week!!!
User avatar
valleydaddy
New Member
 
Posts: 34
Joined: Fri Jul 02, 2010 11:33 pm
Location: Aberdare
Shelter: Outwell Hartford XXL

Re: Electrics and tents

Postby dadoc2001 on Sat Jul 10, 2010 12:25 am

So if peops are unable to take advantage of B&Q'S offer what links would others give to other good value electrical hookups? I have just booked 5 days at Faskally in Perthshire that has an electrical hookup as standard in its pitch charge. May as well get a Hookup before we head out then for our electrical gubbins :lol:
dadoc2001
New Member
 
Posts: 32
Joined: Sun Jul 04, 2010 10:44 pm
Shelter: Outwell Hartford L

Re: Electrics and tents

Postby Wayne on Sat Jul 10, 2010 6:25 pm

Take a look at this review and if you like it click on the Amazon link for a good price of £45.

Also take a look at Towsure the have a deal on it.


Image
15m is usually enough, but so often it can be too short so its always worth considering an additional extension lead, this one is £22.45 and comes with a bag




Nope, never took it out of the box. But, the salesperson said this tent was super easy to set up; even in windy conditions...
User avatar
Wayne
Site Admin
Site Admin
 
Posts: 4890
Images: 484
Joined: Thu May 28, 2009 11:31 pm
Location: Derbyshire
Shelter: One of each

Re: Electrics and tents

Postby dadoc2001 on Sat Jul 10, 2010 10:52 pm

Thanks Wayne.

I had been looking at Sunncamp Hookups but the traditional scotsman is always trying to pay less :lol: . I have been watching a few of these on Ebay and they are going for £40-45 so clearly Towsure is the best bet. Cheers 8-)
dadoc2001
New Member
 
Posts: 32
Joined: Sun Jul 04, 2010 10:44 pm
Shelter: Outwell Hartford L

Re: Electrics and tents

Postby Wayne on Sun Jul 11, 2010 2:53 pm

dadoc2001 wrote:but the traditional scotsman is always trying to pay less :lol: .


:lol: :lol: :lol: , your welcome




Nope, never took it out of the box. But, the salesperson said this tent was super easy to set up; even in windy conditions...
User avatar
Wayne
Site Admin
Site Admin
 
Posts: 4890
Images: 484
Joined: Thu May 28, 2009 11:31 pm
Location: Derbyshire
Shelter: One of each

Re: Electrics and tents

Postby dadoc2001 on Sun Jul 11, 2010 4:13 pm

Thanks again Wayne. After 'watching' a few new (and used :o ) Sunncamp H.U's going fro around £40 BEFORE P&P decided to order directly from Towsure this afternoon (£43.95 delivered). Tent is gonna be like a home from home now :lol:
dadoc2001
New Member
 
Posts: 32
Joined: Sun Jul 04, 2010 10:44 pm
Shelter: Outwell Hartford L

Re: Electrics and tents

Postby ChrisR on Sun Jul 11, 2010 9:24 pm

Wayne... What's your opinion on these..

http://www.gooutdoors.co.uk/mobile-mains-kit-p155317
User avatar
ChrisR
Active Camper
Active Camper
 
Posts: 155
Joined: Sun Jul 11, 2010 9:52 am
Location: somerset
Shelter: Hi Gear Corado 8

Re: Electrics and tents

Postby in-a-tent on Sun Jul 11, 2010 9:31 pm

That looks like the Suncamp one we have, I assume it's a 25mA RCD not a 25A like it says in the details. (Ours has a 30mA RCD and pole 10A MCB)
User avatar
in-a-tent
Addicted Camper
Addicted Camper
 
Posts: 3214
Images: 1
Joined: Thu Mar 12, 2009 8:34 am
Location: The Fens
Shelter: Trigano Vendome

Re: Electrics and tents

Postby Wayne on Sun Jul 11, 2010 9:48 pm

in-a-tent wrote:That looks like the Suncamp one we have, I assume it's a 25mA RCD not a 25A like it says in the details. (Ours has a 30mA RCD and pole 10A MCB)


Yeh I would think it means 25mA, which is a bit delicate, 30mA is the normal and is actually the one fitted as standard and by law to dwellings. Basically it means it will allow 25mA to flow to earth (or an inbalance between L and N if you prefer) before it trips, 30mA is bad enough. When you consider that everything leaks to earth and electronic stuff is the worst.

ChrisR wrote:Wayne... What's your opinion on these..

http://www.gooutdoors.co.uk/mobile-mains-kit-p155317


Yes it looks OK from the picture, but I like to have a hold of stuff like this before I fully commit myself. What's that I ear you say, I should go to "Go Outdoors" and have a look :lol: . As Andy say's it does look like the Suncamp one which is on a sale at Towsure at the moment.




Nope, never took it out of the box. But, the salesperson said this tent was super easy to set up; even in windy conditions...
User avatar
Wayne
Site Admin
Site Admin
 
Posts: 4890
Images: 484
Joined: Thu May 28, 2009 11:31 pm
Location: Derbyshire
Shelter: One of each

Re: Electrics and tents

Postby t4newbie on Sun Jul 11, 2010 10:55 pm

I bought one of these today from Go Outdoors
http://www.gooutdoors.co.uk/pennine-lei ... scTabSect1

I plan on using it in my van, as a cheaper alternative to a properly installed hookup etc. Anyway, on reading the small print it states "Do not use outdoors". I assumed this meant don't use the sockets outdoors, but I can't see anything that says it has IP44. What would be the point of an indoor hookup kit?? Go outdoors have marketed it as an outdoor camping product. Is it safe with no IP44 and that statement on the instructions?

I plan to use it for running an electric coolbox and charging phone, camera battery, maybe laptop etc. I don't want it to blow everything up when it rains. It seems to be made by a reputable firm (http://www.plsgroup.co.uk/index.php?_a= ... roductId=9 ) and sold by a lot of outlets - is it really an indoor-only lead...? :(
t4newbie
New Member
 
Posts: 1
Joined: Sun Jul 11, 2010 10:48 pm
Shelter: VW T4

Re: Electrics and tents

Postby Wayne on Mon Jul 12, 2010 7:10 am

t4newbie wrote:I bought one of these today from Go Outdoors
http://www.gooutdoors.co.uk/pennine-lei ... scTabSect1

I plan on using it in my van, as a cheaper alternative to a properly installed hookup etc. Anyway, on reading the small print it states "Do not use outdoors". I assumed this meant don't use the sockets outdoors, but I can't see anything that says it has IP44. What would be the point of an indoor hookup kit?? Go outdoors have marketed it as an outdoor camping product. Is it safe with no IP44 and that statement on the instructions?

I plan to use it for running an electric coolbox and charging phone, camera battery, maybe laptop etc. I don't want it to blow everything up when it rains. It seems to be made by a reputable firm (http://www.plsgroup.co.uk/index.php?_a= ... roductId=9 ) and sold by a lot of outlets - is it really an indoor-only lead...? :(



Yes its OK, you are relying on the fact that the EHU point you plug into has an RCD and also over-current protect, which is acceptable. Its say's its for in-door use because it does not have an RCD built in to it, but if you are protected by the site EHU points RCD then its fine to use outdoors. Also when an item say's it is IP44 that means without anything plugged in and the flaps closed. You would use a normal extension lead plugged into your mower in the garden and that has no IP rating against rain, but then you don't mow in the rain.

`Image Image

This is a true water resistant plug and socket for outdoor use by Lewden, (IP66 and can take a direct hosepipe hit)

Image

Same with this Masterseal socket, it allows a standard plug to be inserted and then the lid closes and seals around it making it safe against most water and offers IP56 with the lid closed.

So the bottom line is, if you are plugging into a EHU that looks like its been maintained and the unit is in your tent / caravan for use with basic camping stuff as you mentioned then you will normally be OK assuming the site tests its equipment :D . I have to be honest and admit that my EHU set up relies on the campsite and I don't have my own RCD, although It is one item I plan to upgrade at some point.




Nope, never took it out of the box. But, the salesperson said this tent was super easy to set up; even in windy conditions...
User avatar
Wayne
Site Admin
Site Admin
 
Posts: 4890
Images: 484
Joined: Thu May 28, 2009 11:31 pm
Location: Derbyshire
Shelter: One of each

Re: Electrics and tents

Postby Rob-merlin1973 on Mon Jul 12, 2010 9:20 am

I have to be honest and admit that my EHU set up relies on the campsite and I don't have my own RCD, although It is one item I plan to upgrade at some point.


Naught naughty ... :o

Have to admit mine is the same :oops:

home made with blue plug , 25 metres of cable and a double socket. :D
The Camping Forum Campout 2012 ....... Check it out .... Here
User avatar
Rob-merlin1973
Site Admin
Site Admin
 
Posts: 4963
Images: 299
Joined: Wed Apr 29, 2009 11:46 am
Location: Coseley, west midlands
Shelter: Vango Infinity 800

Re: Electrics and tents

Postby in-a-tent on Mon Jul 12, 2010 10:00 am

We've got a proper EHU with RCD and MCB and it's IP44, and it clips to the poles ... now, where is the smug looking smiley
User avatar
in-a-tent
Addicted Camper
Addicted Camper
 
Posts: 3214
Images: 1
Joined: Thu Mar 12, 2009 8:34 am
Location: The Fens
Shelter: Trigano Vendome

Re: Electrics and tents

Postby Wayne on Mon Jul 12, 2010 9:40 pm

merlin1973 wrote:
I have to be honest and admit that my EHU set up relies on the campsite and I don't have my own RCD, although It is one item I plan to upgrade at some point.


Naught naughty ... :o

Have to admit mine is the same :oops:

home made with blue plug , 25 metres of cable and a double socket. :D


Do you plan to replace it at some point with a proper EHU unit (you can still turn your existing lead into an EHU extender if you get a blue socket, which I might have in the shed ;) )
I guess like everything you slowly improve and build your kit over time and for me the home made bit was a quick fix, which I do feel a little ashamed of.

in-a-tent wrote:We've got a proper EHU with RCD and MCB and it's IP44, and it clips to the poles ... now, where is the smug looking smiley


True, true. But out of interest. Have you a certificate for your set-up to confirm its been tested. I'm betting No, they do not normally test them as it lies to you to confirm it works every twelve months (might actually be 6months for camping and caravan sites, will have to check the regulations tomorrow.

Which just gives me a thought, which I'll mention over on the camp-out page.




Nope, never took it out of the box. But, the salesperson said this tent was super easy to set up; even in windy conditions...
User avatar
Wayne
Site Admin
Site Admin
 
Posts: 4890
Images: 484
Joined: Thu May 28, 2009 11:31 pm
Location: Derbyshire
Shelter: One of each

PreviousNext

Return to Camping Equipment

  • Similar topics
    Replies
    Views
    Last post

Who is online

Users browsing this forum: No registered users and 1 guest